  • January 24, 2017

我們有一台 APC Smart UPS 1500。“更換電池”指示燈亮起,apcupsd 報告:

Emergency! Batteries have failed on UPS xxxx. Change them NOW

然而,從這篇文章中,

http://sturgeon.apcc.com/kbasewb2.nsf/for+external/f39c4312fcaf7b948525679a005ebb78?OpenDocument

似乎還不清楚是否需要更換 UPS 電池。更奇怪的是,根據 UPS 上的資訊,在 27.7V 下執行 42.9% 負載下執行 11 分鐘還不錯。

關於接下來要嘗試什麼的任何想法?我們是非營利組織,金錢一個對象。更換剩餘一年左右的電池將是一種恥辱。

# apcaccess status
APC      : 001,041,1017
DATE     : Thu Mar 29 13:01:41 EDT 2012
HOSTNAME : oreilly2
VERSION  : 3.14.6 (16 May 2009) debian
UPSNAME  : xxxx
CABLE    : Custom Cable Smart
MODEL    : Smart-UPS 1500
UPSMODE  : Stand Alone
STARTTIME: Thu Mar 29 12:57:30 EDT 2012
STATUS   : ONLINE
LINEV    : 112.3 Volts
LOADPCT  :  42.9 Percent Load Capacity
BCHARGE  : 100.0 Percent
TIMELEFT :  11.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
OUTPUTV  : 112.3 Volts
SENSE    : High
DWAKE    : -01 Seconds
DSHUTD   : 090 Seconds
LOTRANS  : 106.0 Volts
HITRANS  : 127.0 Volts
RETPCT   : 000.0 Percent
ITEMP    : 23.8 C Internal
ALARMDEL : Always
BATTV    : 27.7 Volts
LINEFREQ : 60.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT  : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
SERIALNO : AS0603298896
BATTDATE : 2006-01-14
NOMOUTV  : 120 Volts
NOMBATTV :  24.0 Volts
FIRMWARE : 601.3.D USB FW:1.5
APCMODEL : Smart-UPS 1500
END APC  : Thu Mar 29 13:02:12 EDT 2012

執行 upstest 時出錯

You are using a SMART cable type, so I'm entering SMART test mode
mode.type = USB_UPS
Setting up the port ...
Hello, this is the apcupsd Cable Test program.
This part of apctest is for testing Smart UPSes.
Please select the function you want to perform.

1) Query the UPS for all known values
2) Perform a Battery Runtime Calibration
3) Abort Battery Calibration
4) Monitor Battery Calibration progress
5) Program EEPROM
6) Enter TTY mode communicating with UPS
7) Quit

Select function number: 2

First ensure that we have a good link and
that the UPS is functionning normally.
Simulating UPSlinkCheck ...
YWrote: Y Got:
getline failed. Apparently the link is not up.
Giving up.

執行一個破敗測試。這將告訴您電池的實際執行時間,而不是理論執行時間。它將負載切換到電池,並執行直到剩餘執行時間或電池電量達到最小允許值,此時它將切換回主電源並為電池充電。

除非電池立即失效,否則您不應該有任何停機時間。

為此:

  • 停止 apcupsd 服務
  • apctest
  • 選擇Perform battery calibration

引用自:https://serverfault.com/questions/375038